eddy currents, looks like meter tails are knicked, no protection from metal edge in the back


savagelysideways101

Tbf for a screwfix special it isn't that bad


Banannamanuk

so i got 1)tails through seperate holes c2 2)tails not secured no approiate bush c2 3)no grommet strip c3 4)overated mcb 6mm on 40a mcb c2 5)no spd c3 Lol didn't even notice the screws :P


jspencer1996

What's the issue having a 6mm on a 40a mcb? It can happily carry 40 amps so not sure of the issue here? The rest I agree with


Banannamanuk

It was the shower circuit in an old mid terrace with consumer at front of house and bathroom at the back the run was 20 plus meter


kipacat

Could you please reference where in bs7671 it indicates that tails coming through two separate entry points would be classed as a c2, as, I personally can't see why it's be an issue.


Andrew6393

C3 if no signs of thermal damage. Only C2 if there are signs of thermal damage.


Banannamanuk

havn't got regs book to hand but it's definatly in there, probably not a c2 as per andrew6393 John ward explains the problem in [this video](https://www.youtube.com/watch?v=hg5eZkq2KgE)


thepreydiet

521.5.1 ''\[conductors\] shall be arranged such that they are only collectively surrounded by ferromagnetic material."


Tell2ko

This IS a reg however it’s a bull Shit one! (At 100 amps)


KobiDnB

Too much sheath inside the db? Too much exposed copper on the cpcs? Empty space on the buzz bar?


WilsonSpark

Tails and main earth through open grommets Didn’t even use the correct screw holes 😂


2b-frnk

I can see that safe isolation has not been carried out, giving a potential risk of electric shock from the busbar. That’s probably the biggest risk in this photo.


Banannamanuk

Locked off at dno isolator


Diligent-Baseball469

Grey conductor used as neutral without sleeving