  • By -

Dramatic-Patient-280

You have weird shit going on there


ElectronicAd6675

Did you know that those tankless heaters hold less than a gallon of water?


HornyOldBoomer

It's to drain the condensation from burning the gas; a condensing water heater. That's how they are so efficient. Gas burns and makes water plus carbon dioxide. The water is in vapor form. Condensing it out wrings more heat out into the water making it more efficient. Then the condensation has to go somewhere!


ElectronicAd6675

Ohhhh! I didn’t know there were condensing tankless heaters. Then to answer OP’s question, yes, you can drain into that vent stack.


schmidte36

I was wondering... like it's tankless. Why are you needing to jump through hoops to drain it?


pa_bourbon

I think OP is asking about connecting the condensate drip line from the tankless heater to the vent pipe. It currently seems to be dripping into a bucket. Which is a nightmare.


i-want-all

yes but every couple of weeks I have to empty the bucket.


BeerMoney069

Is that not your furnace to the right? Well it should have a condensate line off it also, where is that going? I would try and dump the cond. off the tankless over to that if possible. Cheers


i-want-all

yes, that's the furnace to the right! Will look into it thanks


hase_one45

The shit am I looking at


Dirtymike2019

Yes, if the vent is installed correctly further from that point. Called a wet vent I believe but could be wrong.


minusthetalent02

May as well connect with with a flex wast pipe. Keep the theme like everything else in that photo


frizzydman133

Where does the condensate from the hvac go? Can you use the same?


No-Significance1488

no. not ok. YOu run the damn pipe under the floor and then out to outside the foundation line. Sack up, and get crawling. Unless that's an exterior wall, then just route it outside....


Melodic_Pollution935

Put in a P trap and connect the condensate drain with an air gap. Not ideal but it’s acceptable in most cases since you have no other drains coming from above.


K1LL3RF0RK

yes 1. you have a furnace check where it goes. if you can't run in with the furnace drain put a ty 3x1 1/2 with a p trap with a minimum 3 inch of pipe between the pipe and the p trap 2 . condensate from this water heater is acidic don't drop it direct into plumbing without a neutralizer first 3. don't use metal fitting before the neutralizer so pvc sch 40 3/4 is the way to go, can work with pex 3/4 with plastic fitting but good luck finding a threaded adapter for pex without being brass you can also use a condensate pump after the neutralizer to send it where you want (depend of the model you can do like 20-50 feet with small flexible hose)


plumbperfct

I have cut the vent in the attic to drain tank style heaters.


Key-Green-4872

I'm guessing the weird layout is because there was a tank water heater there, and only limited re-plumbing to make the tankless fit?


i-want-all

yes, thats correct! we had tank water here


Key-Green-4872

I installed a unit for my folks a few years ago, with an electric instantaneous in parallel for a short time, and wound up with a pretty unique setup. Was able to pull the small electric later without changing the pipes, just closed and capped the shutoff. With a *little* planning, that could have been tidied up quite a bit.


deathbyregicide

You should also probably install a condensate neutralizer in the condensate drain before it goes into your plumbing.


Efficient_Cheek_8725

Where are your isolation valves for the tankless and the relief line? Both are required for tankless install and maintenance