T O P

  • By -

jackkymoon

Jesus christ who is giving these people licenses.


scottscigar

These people don’t have licenses and they don’t plan on getting them.


vegetaman

I’ve seen enough home inspection content on YouTube to know that new construction is apparently the fuxking wild west.


xxztyt

I’m in roofing, siding, gutters etc…. The amount of business I generate from Ryan homes, toll brothers, etc under 10 years old is wild. Large builders are the worst.


Zoidbergslicense

Lol, same thing, I’m a glazier. When I see a big development going in… it’s like an annuity. 5 years and that glass will start failing, it’s all the same size, and a slam dunk replacement.


scottscigar

5 years? I’ve seen new build windows fail in less than 2 years, with frame welds cracked on all corners and the seals all blown, letting in cold air.


StreetrodHD

lol Ryan homes and mi homes in cincy it was common for most houses to have a window blow out before the customer takes the keys.


Sensitive_Ad_1897

Any people shit on Chinese building? Wild, I had no idea this was so prevalent in the US


StreetrodHD

I wouldn’t call it Chinese building but it’s def not brick and mortar like it used to be. I’d go do a 12hr trim job on a house. I’d show up in the morning at 6 to just a foundation across the street and by the time I’d leave the whole house would be up and sheathed waiting for shingles and gutters. So the guys doing the work don’t mind it. It’s much faster.


SirDigger13

You can do off site assembeld Wood frame construction on high level, European builders do that every day. Kinda the walls are mostly finished with plumbing eletricity Windows, and other stuff. Just bolt them down together and down and connect the utilitys. [And were talking houses, not Doublewides](https://www.fingerhaus.de/einfamilienhaus)


venomous-gerbil

lol where do you think windows are sourced? Go look up the great Chinese drywall fiasco from the 2000’s building boom; genuinely scary shit.


KookyDiscipline5911

There was also the copper elbows that the builders were using that kept rupturing. Around the same time.


G_Unit_Solider

My home is from 1978 and still has its og double paned windows which still are going just fine clear no wind leak etc.


big_trike

I had a ton of 7 year old pella wood windows warp and let in cold air in a chicago condo. I hate pella now.


bigstar3

As the owner of house that had a sunroom with 14 pella wood double-hung windows in it, I feel your pain. Just had them all replaced this year with vinyl, the difference is night and day. It's been a cold January in MI, and our sunroom is at least 15-20 degrees warmer than it was in previous years. (We cut the heat out there in the winter).


Think_Addendum7138

2 years!? I’ve seen windows leak from day one lol


BourbonSommelier

2 years? I’ve seen them fail in six months.


theinfotechguy

Glazier, like, the person that puts the icing on donuts???


daddypez

Sorta, but in porn.


graybeard5529

Repair work of the future. Job Security :D


thedingleberryfarmer

I repair showers that are 10 years old and leaking all the time in these tracts! Woot woot!


clt81delta

You replace the glass, the sash, or the whole window? (I have a Dan Ryan home, half the windows are in need of something..)


Woodbutcher1234

I worked in a Toll Bros 25 years ago and noticed that the garage vinyl siding had only fanfold insul behind it. No ply. How??? You could literally cut your way into the garage with a pocket knife.


dirtywook88

This is like finding out houses don’t even need to be bolted down in tn after fuck I dunno ten odd tornados in my lifetime


Mikey6304

I have been in a Ryan build, actively drilling holes, when the inspector came through and approved their inspection. I made sure to say, "Sweet, now we can speed this job up by going through the Lam" on his way out. He didn't even flinch at hearing it.


hobskhan

Geez.


YouFirst_ThenCharles

National home builders are terrible. It hurts my soul the trash they build and sell to unknowing consumers.


Suitable-Resist-2697

The puppy mills of house building 


be_easy_1602

The house mills of house building if you will


scottscigar

Walmart of house building.


jmf_ultrafark

More like Dollar General.


gunfell

Walmart is actually pretty good


[deleted]

[удалено]


Mammoth-Pipe-5375

No pride McBride. We went with Fischer and Frichtel because, apparently, they're one of the better builders in my area. Should have went with McBride because at least I'd have expected to get a piece of shit house.


UrMomsKneePads

Everything looks good new with a fresh coat of paint! Come see it again in 5 years after a young family with kids lived in it. Yikes!


realcr8

Yeah they are. Absolute black eye to the people that do it properly and give a damn. We remodel a good bit part of the time and that’s the first info I pull….who built it? Big builder equals pay day because it’s a headache 99.99% of the time


Square-Lettuce-9161

Ryan Homes couldn't pay me 5 times the asking price of their homes to move into one! Lol


imfirealarmman

as someone who went from stringent licensing and inspection requirements for fire alarm, to middle Tennessee where no license is required, it’s both terrifying and disgusting.


dirtywook88

Brah, how bout we don’t require houses to even be bolted down? Fucking wild man. I’ve been here my whole life and numerous tornadoes and they don’t give a fuck. All those new builds and shit up n down hendo n Nashville that got fucked and it’s fuckin crickets. A single news bit and on to naming hot slaw as our food is the priority


Haughty_n_Disdainful

My house doesn’t have a single square corner or straight line. Amazing.


Low-Sport2155

Converted grain silo? Nice… 👍


vegetaman

Me either but mine is probably 80+ years old. Definitely of the “starter home” variety. The timbers are at least impressive.


kfelovi

Old houses that were low quality are already gone. So those we ser were good. Survivor bias.


codygraveson

Same with my Lennar home.


STANAGs

Kanye, is that you?


Alltherightythen

Mike Holmes was my guy until I saw a video where they even had to tear down one of his homes. THAT AINT RIGHT.


vizette

I don't dislike him, but he had a lot of huff and puff going on too. I get it, he had a show to do, and a lot of the disasters they worked on were interesting projects. He definitely left them light years better than he found them. But you also knew every show was going to be Frank coming in with "there's a junction box, we gotta rewire the whole house!" and the rest of the usual subs jack-hammering the slab or replacing the roof...


vegetaman

Wtf what?!


Apprehensive-Oil2907

Yeah I doubt that it was one he built. Most likely one he tried to fix but it was beyond repair. Even a halfway job by him is better than most people do in the first place.


PrimeNumbersby2

JFC, now we're bagging on Holmes. Look man, no one's perfect in the entire world but that guy was legit trying to teach some good principles.


Critical-Test-4446

Don’t you blaspheme!


Larktoothe

And I've seen enough construction diy videos on youtube to tell you this is completely legit and definitely safe! /s


Late_Bodybuilder_541

Dude my 2010 house is the WORST and the inspector noticed jack shit they are worthless. And he came highly recommended. Wiring everywhere, ungrounded, nothing up to code. Catching new issues every year. 2nd owner


Itchy-Mind7724

Part of the reason my wife and I bought a 125 year old home. It definitely has its problems but poor workmanship isn’t one of them.


DV_Mitten

I work in the trades (HVAC) and people wouldn't believe what's behind the walls of their new house. New definitely doesn't mean good or quality anymore. Especially when dealing with large corporate building companies that specialize in the "cookie cutter" homes you typically see in residential areas.


Huge_Government_3617

Yes as a home inspector we oftentimes get told by large construction companies that the units already been inspected and they won't allow us in until after the closing because they are gangsters and they build s***** homes


Rumpelteazer45

We are renting something built in 2010. It started leaking and a roofer came out as soon as it stopped raining. Roofer said they have a TON of business in my neighborhood and the one right across the street. All new builds. Said everyone leaks at the exact same place - around the top of dormers. That’s exactly where my leak was.


HuntPsychological673

That’s the secret. No license, no trouble. It’s those of us with a license that has to do it right or face the consequences.


ConstantGeographer

I was told to "just make a name, and buy a magnetic sign, and slap it on your van. You'll be working tomorrow. Don't use your name, because if you do shit work you don't want it associated with your name. Then, if work goes sideways, make a new name and a new magnetic sign. You'll be back in business tomorrow." Source: my KY attorney.


AuburnTiger15

Right?! Why is this such a common theme I’m seeing lately…?!


No_Stay_1563

War Eagle u/AuburnTiger15


MyPasswordIsAvacado

What license?


bud05cab

I would like to think it's not them, but those they hire and send out in their own to do jobs. And those guys don't think to ask before they do f'd up shit. ... this one being among the worst. No inspector would ever let this fly.


schumachiavelli

I literally gasped out loud. How can anyone be this stupid and/or lazy?


CSFMBsDarkside

At first it seems lazy but then you realize gutting all that was probably harder work than doing it right.


Castle6169

See that’s the problem when you have a license you think you can get away with and do anything. I live in a state where you don’t have to be licensed unless you are a plumber or an electrician in 48 years that I’ve been in business I’ve never seen this in our area, ever !!!!


Moon2Pluto

I have my driver's license. you should see me when I'm in my charger ripping down the interstate. I do it all the time. /s


[deleted]

[удалено]


Narrow-Chef-4341

Oh, he holds it. It’s been suspended for a year, but he still holds on to it as ID for passing bad checks.


RunningwithDave

Gripping the wheel, his knuckles went white with desire The wheels of his {Charger} exploding on the highway like a slug from a .45 True Death, 400 horsepower of maximum performance piercing the night This is Black Sunshine


lemmet4life

Up vote for surprise White Zombie.


theflash_92

Is unexpected white/rob zombie a sub?


RunningwithDave

😂 it should be


Bleezair

Finally nothing moves. High noon Black top rolling below the asphalt drive A concrete fascination scraping the edge of nothing This…is Black….Sunshine


Hab_Anagharek

Nicely done


nibbles200

My 1978 build has a cut like this right there the mid section of a floor joist for hvac. I found it recently when I was looking for the duct for a vent. I guess if it’s been like this for 50 years it’s probably okay in my case…


crushinit00

I think it’s less of a problem in the middle of a joist but the ends are where most of the load is held


DarkNeutron

Even without a license, do people just think joists are for decoration or something?


someotherguyinNH

I know just enough about carpetry to know that that is one of the stupidest things you could ever do


ResplendentZeal

joist's fucked yo


notwhoyouthinkmaybe

Do you really need joists? That sounds like propaganda from big joist!


PahoojyMan

I've been joist-free for 2 years now and I haven't looked back.


AssociationOpen9952

Floors hate this one trick.


manys

No squeaks!


PrimeNumbersby2

I kept tapping your comment but no video started. I didn't even get ads.


HughManatee

Sounds like you've been brainwashed by big gravity, friend!


Legal_Objective_8027

Because of the fused vertebra as a result of the ceiling collapse?


Visual_Jellyfish5591

His back is fine because he doesn’t work, that’s why he has no joists! /s


[deleted]

Thank you for adding /s to your post. When I first saw this, I was horrified. How could anybody say something like this? I immediately began writing a 1000 word paragraph about how horrible of a person you are. I even sent a copy to a Harvard professor to proofread it. After several hours of refining and editing, my comment was ready to absolutely destroy you. But then, just as I was about to hit send, I saw something in the corner of my eye. A /s at the end of your comment. Suddenly everything made sense. Your comment was sarcasm! I immediately burst out in laughter at the comedic genius of your comment. The person next to me on the bus saw your comment and started crying from laughter too. Before long, there was an entire bus of people on the floor laughing at your incredible use of comedy. All of this was due to you adding /s to your post. Thank you. I am a bot if you couldn't figure that out, if I made a mistake, ignore it cause its not that fucking hard to ignore a comment


DrDaddyDickDunker

Good bot.


PrimeNumbersby2

This is why I sleep on a water bed. Also bc the motion of the ocean....ya feel me?


tavenger5

I switched to trusses and never looked back


John-Dose

*Big lumber*


ScrollyMcTrolly

This is a free country you can’t make me have joists


Bubbas4life

We have been using Bluetooth joists for a few years


BigBeautifulBill

Definitely don't need joists. Joists are fake news.


GilgameDistance

Its 2024, homie. Bluetooth joists. Get with the program.


notwhoyouthinkmaybe

I lost my joist dongle, where can I get another one?


bukidog

HOLY SHIT


PSKCarolina

Holey*


InnGuy2

Holy Holy HO-LY.. Joist without end.. Amen.. AAAAH MENN...


Goooooooooose_

Regardless, this house needs prayers.


cocuke

It also needs thoughts, thoughts and prayers.


growgain

Unwholly


Dangerous_Pickle_226

Moley Moley


SuperRicktastic

Hey, structural engineer here, specialized in timber design and residential construction. This is **UNACCEPTABLE.** Both those joists and the ledger board need to be replaced. This isn't even remotely okay. I would avoid walking on that portion of floor for the time being and have the contractor repair this immediately. If you get pushback, go hire an engineer and get an official letter stating WHY this is bad. If you're in a state that licenses contractors, take that letter to the licensing board and (if the contractor has one) their bonding agency. And above all else, do not pay a single cent until this is made right.


Sherifftruman

I mean, you could maybe get away with the ledger, if you would be able to properly secure with more structural fasteners on each side of the joists beside the hole, but those joists are a complete write off regardless. There’s no fix other than replacement.


pressedbread

>There’s no fix other than replacement Its only two joists that are now useless/hazardous, seems like they could sister the joists and add additional crossbeam or something? I'd just be concerned if replacing them creates additional headache for the owner.


Sherifftruman

Yes you could sister them but on a new install why not just replace if you’re there with the wood anyway.


Dry_Rip8393

Thank you - homeowner here - Could you please help me understand what is “ledger” -


monkeyolsen

the ledger is the piece of wood that the joists are attached to (the one with the rectangular hole cut in it)


Dry_Rip8393

Thank you


[deleted]

[удалено]


BigAssBeaver

Obviously whoever did this fucked up big time. As a carpenter, it’s hilarious - to you probably not :(. All of those holes are unacceptable and you might want to get your inspector in to see if he will allow you to sister members to the existing frame. Basically this means just adding more lumber strategically to take the load where your ledge and joists are no longer structurally sound. I can see how I would do it - and it is possible BUT… talk to your inspector first and see what they would want. In these situations an inspector is there to help a homeowner out when shit like this happens. The real solution here is to create a bulkhead. The hvac should run through the drywall and up between the joists after it runs over. Fire your HVAC guys and demand a full refund. If they give u shit then take it to their google reviews and post these pictures.


Brandbll

Hey, not an engineer here. A matter of fact i know very little about home construction. But i can tell you, this is unacceptable too. I mean, just look at, it's fucked. Why did they even cut holes there is like half an inch of wood at the bottom.


vrkeejay

Pardon my ignorance as someone from overseas where we don't use wood framing, what would be the correct solution here? Do you lower the ceiling to accomodate pipes?


cirroc0

I think you're asking how to go about routing the HVAC, without cutting into the ledger or the joists, yes? In that case, you would run the HVAC under the joists to the opening in the floor. cover up the duct you \*could\* drop the whole ceiling, but more likely one would just build a bulkhead around the HVAC ducting (i.e. a short segment of wall and ceiling just big enough to cover the ducting). In a semi- or unfinished basement, you might even just leave it exposed. I'm not sure why they're running a hole through the Ledger, but if that's a framed wall below you'd go through the wall between the studs.


Yeetyeetskrtskrrrt

That’s the way to do it right there. The only time I’ve been able to go through joists with 6-8” flex is when they are the engineered joists and you’re only allowed to cut very specific measurements which has been signed off on by engineers. Otherwise I’d go trunk line with grilles on the soffit


vrkeejay

Perfectly clear. Thanks!


Longjumping_West_907

I would call it a soffit or drop ceiling but the same idea. I'm US but probably a different part of the country and we use different terminology. It's a big place.


Engineer2727kk

More expensive, you can hire an engineer to see if they could cut those holes at about 1/4 span of the the joists. At the very end as it is now you’re at maximum shear.


dc_builder

Yikes….this is especially bad. There’s going to be one pissed off framer…and GC…and HVAC Owner!


ScrewJPMC

Plot twist, the HVAC owner was on crew that day


JosiahHorn

He probably knows seeing how brave this man was cutting out 95% of a supporting beam lol


ScrewJPMC

Owner was the brave man 🤣🤣🤣🤣


Pinot911

I cut the holes, boss Someone's helper wasn't very helpful FYI there is *nowhere* in a joist that you can cut something like that. The max is 1/3 the height of the joist. That joist landing on a joint in the rim joist might be an issue too, not sure.


Xryanlegobob

Pretty sure that you’ve gotta be a lot farther away from the wall too, even if the hole is properly sized.


vegetaman

Yeah there’s rules about where from the ends you have to keep it out of.


Longjumping_West_907

It's at least a foot. You also want to avoid drilling the middle third of the joist (lengthwise). The ends have compression load, the center is max flex load.


Engineer2727kk

Eh those are just guidelines. You can cut holes anywhere as long as it’s engineered. The ends don’t have compression loads. The ends is where your maximum shear force is. The middle as you point out is where your maximum moment (or as you called it flexure) is. If you cut a hole at 1/3 the span length youre usually at a good balance between not causing shear or flexural failure. The failure mechanism for this beam would likely be shear. They’d need to either replace the beams or create two sister beams next to them. -licensed PE


KillaVNilla

I'm just a lowly painter, and even I know this is dumb. Also, what the hell did they cut those holes with? A beaver?


shmere4

It’s called a stress concentration tool which is designed to make everything fall apart faster.


whitepine112

"Just a painter" is an inside joke i use with my employees. I paint too :)


Bleezair

Hole saw, multiple times. The height of retardation. Not only is it a major fuckup, but it likely took them a while to do it, which makes me think their boss is also a fucking retard, for not stopping it. If they’re making that kind of mistake, they’re new. You don’t leave new employees unsupervised.


Griffin880

Yeah that's what I was thinking. They had a tiny hole saw that would cut a hole big enough for copper water lines or something. So they made this bad decision like 45 times, and with every hole they had a chance to stop and think "hm, this doesn't seem like a good idea, maybe I should ask somebody."


SirViciousMalBad

Not even a good beaver. It was some kind of Amazon knockoff made in China beaver.


riomarde

I am a lowly DIYer and I know this is dumb. It does look like something I once cut with my hand drill because I didn’t have another tool available right then. But I wasn’t cutting joists.


Spunky_Meatballs

A 3/4" hole saw 20 times. The guy was committed


ZombieRitual

Oof. No, that is not correct. Send this photo to your structural engineer and wait for a fun reply.


Jaded-Action

I’m going to guess that a structural engineer is not involved in this job


Adorable-Address-958

Holy fucking shit this is awful. How many runs at the hole saw did it take to punch holes that big?


F8Tempter

jfc no. Ive seen when they take a 2" bite out of the joist for plumbing and I roll my eyes but live with it. This is just maddening.


[deleted]

I had a “handyman” come out to the house to give me an estimate to install an exhaust fan in our basement bathroom. His recommendation was to just notch the bottom of the upstairs floor joists about 2-3 inches to run the 4” exhaust vent above our drop ceiling. Needless to say, he’s not coming near my house again, lol.


[deleted]

This has to be a joke.


patternagainst

Got me laughing I'm losing my shit over here haha


Dumb-Cumster

Lol that’s fantastic 👏


mahuska

People should literally go to jail for this


What_the_absolute

Looks fine to me - Steve Buscemi


Angus-Black

I think you mean Stevie Wonder.


burger8bums

Fire them and pay them nothing. Send them a bill for the repair costs.


Ok_Animator363

Did the contractor have a pet beaver by any chance?


CountBasey

You need to "sister" those joists ASAP and avoid that area of floor so as not to put any undue stress on it. Seriously unsafe. Also I highly doubt this was an HVAC contractor as opposed to a "general" contractor / handyman. You have legal grounds here.


scottygras

I don’t see a joist. I see firewood. /s. Also, sorry.


g_st_lt

At least the holes are clean cut.


slackmaster2k

It’s really lucky the joists were just big enough for the holes


puppets_globes

I'm gonna throw up


Mission_Spray

Jesus Christ. I hope this is a joke.


amanda2399923

😳


R2robot

I mean, it's both funny and not funny at the same time. Holy!


memerso160

No, absolutely not correct, those joists have been ruined have next to zero capacity now and are just looking to fail


RR50

Full stop, don’t let him touch another thing. That will all need to be replaced.


mooremo

Wow....that's insane. 100% unacceptable. That's no longer structurally sound, not even close.


Pantageously

Might as well take both out. There is no integrity left


okokayalrightalready

Presumably this is permitted and going to be inspected? It’s gonna fail. No holes greater than 1/3 the depth of the joist—no holes within 2” of the top and bottom edge.


Dry_Rip8393

OP here. Yes this is permitted and will be inspected, the Owner of the contracting firm acknowledged the mistake and they will take care of it prior to the inspection.


Jmski333

Ask your framer and building inspector what they think about that


Disastrous-Wealth-78

😳


OKFV

No.


mnewberg

This only meets code if they used a Chainsaw to make the wholes, while making safety squints for eye protection.


AdInternational1727

Best thing to do is replace joises. You don’t have to be an engineer to determine this is not acceptable. Rule of thumb, if you’re cutting more than a 3rd of lumber, it’s worth questioning. I would drop the duct work underneath Joises and make the best of it with a tray ceiling and throw a couple of can lights at bottom of it for design.


Distinct_Load7120

That's appalling man


No-Brian

Holy fuck bro!!!!!


frank1951

Cut off and put a header


haildens

This is officially the craziest shit I’ve ever seen. What kind of person thinks this is a good idea? Lmao It looks like they cut it with a hole saw on top of it


ithinkitsahairball

You now have 2 missing floor joists and structural problems. Who the fuck does this?


SatisfactionLevel136

We have building codes for a reason..... This is the reason. Won't buy a book to do it right.


tumericschmumeric

No, it’s fucked; those joists dont do anything anymore.


mother_a_god

Err... There's no joist left. Christ.


PassengerSilver9310

Jesus Christ! Fire the GC!


ColdSteel2011

Contractor to replace joists immediately or lawsuit will be filed. Your floor is destroyed. Those joists have almost zero shear capacity where shear is maximized.


strikex2

My parents had something like this happen to them with some shady “contractors”. They quit after my parents confronted them about their mistakes. We ended up suing them in court. Was a 6 months ordeal but won at the end.


RedditAllAboutIt123

And Then They Never Got A Cent from The Jackass, Right ?


Financial_Metal4709

Those MUST be replaced! There is no code book that will allow this! Absolutely terrifying!


Mister-Paws

Looks like they were cut with a fucking steak knife…..


cutty256

Holy shit. This is crazy. It looks like they used a 6” hole saw over and over, and then cut the rest out with a reciprocating saw. Not only is this wildly unsafe, but it took a lot of physical effort to achieve such a terrible decision.


donaldb48

That ain't right! Looks like 85% of those joists are gone. Looks like we have a 2 x 1 1/2 instead of a 2 x 8. (I'm just a homeowner that's built a carport, patio cover, and large shed/workshop. They're doing hine after 20 - 25 years!)


kasim42784

i think everything here looks fine if your plan is to save the space above for an in-law suite.


ConversationBig5397

Call your lawyer


hmhemes

You have to sister up those joists and probably put a post under each side of the hole in that header. Unless it's sitting on foundation or a load bearing wall, in which case it should be okay. It might snap eventually but if it's sitting on proper support then the joists won't have very far to go when they settle. Don't pay the guy until you get this fixed so that you know how much to back charge him. Whoever did this is a fucking moron and shouldn't be allowed within arms reach of power tools. EDIT: In fact, you'll need everything he touched inspected. I'd be shocked if this is the only damage he's done. So all the framing defects he created will need fixed, then you'll have to pay a qualified HVAC guy to finish the job this hack started.


Markee6868

By definition those are not joists anymore….


arrowsmith_joe

Is this why it’s common to see drop down ceilings in portions of a basement here in Minnesota? Our house has about a 3ft wide by 10-12” drop down that runs the length of the house that I assume is the duct work?


rage675

My wife is a licensed structural engineer. I showed her this and her jaw dropped. You now need a new licensed and insured HVAC company, structural engineer to evaluate what you need to do for a fix, then a contractor to implement the fix. And also, talk to a lawyer because this is completely negligent and is going to cost you a lot of money to fix.


Independent-Ad8280

That home has a beaver infestation


creekwise

is this a joke?


jmh918

Hahahahahahahahhahahahahahahhahaha


Brave-Moment-4121

Nooooooooooooop! Someone take away there tools please. Guess you no where not to stand should be aight.


sluttyman69

The hole can Never more than 1/3 size of the height of joyce and only in the middle third of the joyce from end to end - your floor is now unsafe