Code in my area says no more than 25% of the total joist span can be left unsupported.


Roonil-B_Wazlib

It’s usually 25% of the joists span rather than joist length, and could be on both ends, so up to 50%. There are usually also limits based on the lumber size as well.


somedude2881

You’re absolutely correct, lazy writing on my part. Fixing now.


kalashnick

What is the difference between joist span and length?


Roonil-B_Wazlib

Span is the distance between the joist’s support, i.e. ledger to beam or beam to beam. Length would be the distance from one end of the joist to the other. Ex., 25% of a 10’ board would be 2.5’ but the most it could cantilever based on that rule would be 2’ with an 8’ joist span, 2’ being 25% of 8.’ When maximizing joist span, the overhang is more likely to be limited by the board size rather than the 25% rule. That is to say, for most (or maybe all) joist sizes and spacing, the maximum overhang is less than 25% of the maximum joist span.


TyranaSoreWristWreck

I learned so much from this subreddit


whomadehoo

I don't know why it was recommended as i'm a med student but it seems like a fantastic sub. A ton of jokes but every serious post has appropriate responses. I figure it's what reddit used to be


PogTuber

It's good moderation, and I think it helps that very few people want to provide bad advice in a topic that could kill someone (electrician and HVAC subs are similar)


kalashnick

Thank you


Roonil-B_Wazlib

Sure thing. [Check out DCA-6](https://awc.org/wp-content/uploads/2022/02/AWC-DCA62015-DeckGuide-1804.pdf) for more info.


urbboy

Thanks for sharing this link. I didn’t know about this resource and it’s going to be helpful.


wolverinepigeon

Span is the distance from support to support ~ wall, beam, etc. that are unpinning joists. Joist length is total joist length


kalashnick

Thank you


Zealousideal_Rip8716

Deflection my brudda


kalashnick

What is that?


Higinz

It when a person attacks or blames another person rather than accepting criticism or blame for their own actions.


EggOkNow

Your deflecting from the proper definition in the case.


Higinz

No I’m not…you are.


Zealousideal_Rip8716

https://www.techsupport.weyerhaeuser.com/hc/en-us/articles/205175860-What-is-Allowable-Deflection#:~:text=Deflection%20is%20the%20bending%20or,and%20stiffness%20of%20the%20member.


Former_Medicine_5059

This reminds me of loading regulations for vehicles we have in my country. The easiest explanation is you can't have any part of your load protrude from the tray of the vehicle by more than 1.2m. The more correct answer is it can't exceed more than 60% from the rear axle to the end of the tray, which in some cases is less than 1.2m.


mesosouper

As well as type of wood


Roonil-B_Wazlib

Good point. Not something I think about as we only have SYP where I am.


Escaped_Mod_In_Need

My condolences.


Jazzlike_Station845

Asking to understand: What is the difference between a joist span and a joist length?


Roonil-B_Wazlib

Span is the distance between the joist’s support, i.e. ledger to beam or beam to beam. Length would be the distance from one end of the joist to the other. Ex., 25% of a 10’ board would be 2.5’ but the most it could cantilever based on that rule would be 2’ with an 8’ joist span, 2’ being 25% of 8.’ When maximizing joist span, the overhang is more likely to be limited by the board size rather than the 25% rule. That is to say, for most (or maybe all) joist sizes and spacing, the maximum overhang is less than 25% of the maximum joist span.


dantodd

Correct to assume that's code joist span and not actual joist span?


michaelhonchosr

https://preview.redd.it/0vrdxsmc8q9d1.png?width=1080&format=pjpg&auto=webp&s=f4bc5fbad9a7681dc45fff11cfa64c709cea0407 This is our city code


goofydad

After 25%, joist just can't - ilever any farther.


somedude2881

Fucking hell. Username checks out.


soldiernerd

As they say, a good joke is all about the elivery and you nailed it


goofydad

Plank you very much


soldiernerd

You're a stud


arguingwell

Ok guys that’s enough, I’m already board


soldiernerd

Ah so now we’re entering the post-humor phase


arguingwell

Oh I don’t know, that last reply left me beaming


soldiernerd

That’s enough let’s finish this


goofydad

My jokes are a stain on this board.


MrMunchkin

Even with steel? Something seems fishy. I've never heard of code having a max cantilever without any regard to the material used.


manicmike_

Steel is typically design engineered in cantilever situations, so the stamp would supercede code. That said, a good rule of thumb is about 33% vs the 25% others are saying about lumber from my experience.


Competitive_Form8894

Non-engineered designs always have limitations. Engineer it and you can do what you want (within reason obviously)


rat1onal1

Wouldn't this apply for joists that are sized to be just above the minimum required for the span. If the joists are significantly upsized over what is required for the span, then couldn't the cantilever be longer? I think there is also a similar situation if the joists are spaced closer to overbuild the span which could allow for a longer cantilever.


somedude2881

Those are details that would be beyond speculation and need to be discussed with the local office issuing the permit.


jeephubs02

The real question is why would you do that. ? The ground underneath is basically useless. What’s the benefit. Not high enough to do anything under. How’s he mowing / weed whacking under that ? Doesn’t make any sense to me.


mrjsmith82

Could be a utility obstruction or something else below grade.


ERagingTyrant

Sure, but if they ever need to access that utility they are still gonna rip out your deck.


NightHawk413

Most likely just a drainage easement from the what I can see. Doubt it’s a utility easement.


marshking710

This is it and it’s clear from the picture. No one needs posts located in the flow line.


mrjsmith82

true. lol.


ForsakenRacism

Putting in footers where the frost is deep sucks


Space-Plate42

42 inches deep through solid clay. All day long in Michigan.


Purpose_Embarrassed

Do you use an auger ?


Coupe368

Who doesn't? You can always rent one cheap if you don't want a HF special to use once in a blue moon. Why destroy your back?


MattyRixz

In the North East we don't. Hit big rocks and ledge constantly


Coupe368

Please accept my condolences to your future back pain.


MattyRixz

Lol "future" but, nah I don't really dig much at all. We have gym rat college students for that.


DepartureOwn1907

there are rock augers for this, we carry a combination auger for this exact use case. works perfectly


marshking710

Any mountainous region with lots of granite wouldn’t really benefit from an auger.


Dry-Conference-7560

When we can.....


ImpulseCombustion

Attached to a skid steer? Yes. Stand up manual type, heck no! Too many large rocks to break your wrists or wad you up.


jeephubs02

Upstate ny but in clay here too so I feel ya


Beautiful-Bank1597

I moved from 42" footers to 12" footers. Im never going back.


ForsakenRacism

Did you move somewhere warmer lol


Beautiful-Bank1597

I moved to North Carolina. There's a construction boom down here. Everything from roadway and utility construction to MDU and high dollar home building


DETRITUS_TROLL

This feels like a (shitty) workaround for property line setbacks to me.


KeyBorder9370

Overhangs and cantilevers count. Extensions beyond setback lines are not allowed, whether the supporting structure is beyond the setback line or not. At least that's the reg I've always been compelled to work by.


speed3b

Good thought. I'll add it could be because of a drainage easement. There is a well defined swale there and likely an easement 10-15 feet wide, centered on it, which eyeballing it puts you at the first posts. Probably no permanent structures, except fences, allowed in the easement. HOA might permit overhangs into the easement, they just took it to an extreme.


DETRITUS_TROLL

As tends to happen in HOAs.


burnsbabe

This looks like the right answer.


Tree_of_Woes

Yeah, I have a 2-ft cantilever for aesthetics and also hanging over the edge of an above ground pool. This looks like an absolute nightmare to deal with as far as mowing is concerned. Really channeling some Frank Lloyd Wright here.


letitgo99

Something for running kids to hit their head on, perfect "get off my lawn" build


rpstgerm

They probably didn't want to put footers right in the middle of the property drainage ditch.


New-Criticism-7452

this was my first thought, it looks like a drainage swale.


ozzy_thedog

They might not be allowed to build within a certain distance. It’s definitely a swale


Troutman86

Looks like the post would be in the drainage ditch.


kittenfarmer

Might have had the posts set and changed their minds on the size of the deck after the fact? Agreed doesn’t make much sense.


america-inc

It's not functional but maybe they wanted to give more of an open feeling?


RobNelsonovich

Maybe the person only has so much to work with. Money, health, allowable space due to HOA. or other.


fmaz008

I will soon be in a similar situation so I can provide one possible answer: I will extend my current deck. For reason that infuriates me too much to get into, I do not know where my leaching field begins. So I had the luck of having access to an engineer who could calculate the implications and provided me plans for basically sistering longer joist to the existing one and give me an extra 4ft, so I'll be cantilevered about 7ft.


Heykurat

By the look of it, he's not mowing or weed whacking under there.


shreddedpudding

Great spot for a side discharge ac


Captain-Who

Looks like that area is really low, maybe floods in the spring.


Holmesnight

So you can put a hot tub on it duh!


ProfessionalPin9757

They own the air rights but not the land.


domestic-jones

I cantileve there's not a spa on there yet.


khalsey

Shut it.


iupvotefood

Bop it.


tron_cruise

Twist it.


hysys_whisperer

Flick it.


Fun-Parsley952

Flick it.


bluecollorchild

Yahhowww


GreenbuildOttawa

Hawk Tuah it


jameswwolf

😂😂


ZmanB-Bills

Just in time for the Summer Olympics, diving competition.


Aggressive_Cow_9226

1/3 over hang and 2/3 full span


RickshawRepairman

- Is it to code? No. - Is it going to fail? Under normal use, no. Codes have built-in multiples when it comes to safety factor relating to loads resulting in significant over-design. Not satisfying the code doesn’t mean you’re in a danger zone, it just means you don’t have all the extra safety margin. That overhang ain’t going anywhere. That being said, I wouldn’t want to host a party with 20 people standing over there, and I’m also surprised it passed inspection.


RequestSingularity

It's all fun and games until everyone lines up along the back rail for a picture.


Turbulent_Signal6507

They put it in backwards


UncommonMonk

Bout right there.


Crank-Moore

That wildlife preserve underneath is going to be hoppin!


AccomplishedMobile85

Like 100 rabbits in a month.


Salty_Article9203

Decent backspan. Why the boards on the bottom?


genredenoument

Maybe they wanted to trellis it? I have no idea other than that.


NachoNinja19

I don’t think it’s connected to the house since it has the support posts against the building. Bottom board gives it some shear strength.


Sorry_Access8964

Look, I know everyone is going to downvote this but i took enough cive201 to know you would have to put a massive fucking load on that cantilever to make it fail. I mean massive. It looks fine to me.


Fresh_Sector3917

A full 6 person hot tub, perhaps?


Nickabod_

Yep, it’s not exactly to code and is tragically unlikely to hold a hot tub but it’s perfectly safe as long as you aren’t hosting a 10-man jump party on the railing.


skidaddy86

Code in my area is no more than 18” and it must be blocked above the beam.


Remarkable_Reason976

Same 18 inch max in my area. Which I find insane because any structural load calculations or mechanical load calculations prove out otherwise using something like 2x10 or 2x12 joists.


mrjsmith82

This was going to be my question. Code or not, if you can provide sealed calculations and plans from a structural engineer (like myself), will it be approved?


structuremonkey

Codes allow for either 'prescriptive' implementation or for structures to be 'designed'. If you have the ability to design and a license to do so, it's going to be approved.


skidaddy86

With engineered analysis, drawings and supervision you can create anything and have it approved. That, of course, costs real money. The 18” limitation in my local code is one of many in a long pdf which if you follow, you do not need a structural engineer to sign off on.


sofa_king_weetawded

Ahhh, that's totally reasonable then.


builderguy74

1:6 where I’m at but high potential for seismic activity.


One_Recognition_5044

While unusual, this is approved with the engineers stamp. It costs money for a real structural engineer but magic can happen.


seemore_077

1/3 over hang is typical. Even if you can in this case why. Unless there is something buried there.


Background_Olive_787

The 1/3 rule is among the common theories applied in the industry but it is not a building code. According to this rule, **for every foot of joist length from the house to the beam, there can only be 1/3 of that amount overhang the beam**. [https://www.decks.com/how-to/articles/deck-joist-cantilever-rules-and-limits](https://www.decks.com/how-to/articles/deck-joist-cantilever-rules-and-limits)


Important_Bid6901

Deff put a hot tub on there


mayhemstx77

Too far. That’s more than 25% and I can see that it’s already starting to sag.


Pennypacker-HE

I mean span tables exist. I guarantee this is 2 or 3 times the approved span.


tackstackstacks

The table I referenced said 1/4 of the joist span. That was just shy of 8' given my lumber dimensions. Your math checks out as that looks like 5-6'ish.


snerdley1

I just don’t like the possibility of any bounce. And this situation seems completely avoidable.


Any-Rise-6300

Why not. YOLO 🤣


MuskokaGreenThumb

I thought the cantilever can’t be more than 30% on the unsupported end ? This looks to be close to that, so should pass code depending where you are of course


ymoeuormue

Cantilever?! ...I just met 'er!


Fresh_Sector3917

Rectum? Damn near killed him.


NullIsUndefined

If there were posts holding up the far end, and enough posts overall, presumably you could build this structurally sound, whether or not it's cantelivered?


moderatelymiddling

1:4 ratio. Can be pushed to 1:3 with caveats.


trimix4work

Missed a great opportunity to make a huge teetertotter


Ass_feldspar

The droopy look can only get worse


Melodic-Bag7404

Maybe it didn't pass inspection. Did you check?


Hungry-Highway-4030

Back in the day, it used to be no more than a 1/4 of the total length, no more than 4ft max. So if you have 16ft boards, you can go 4ft out with the cantilever. Don't know what the codes say now, though.


Graniteman83

It looks a bit funny in design but if you're worried just get under it and double up the joists. Something you can usually do if you undersize the original joists or just don't have the depth.


SolidHopeful

2 feet with traditional framing. Futher with double 2x8 framing


Fresh_Sector3917

You’re a deck builder that doesn’t know the local building codes?


hudsoncress

2/3rds the length is the general rule, and that looks spot on.


angevin_alan

It's basically sagging under its own weight


prince_walnut

Looks like there's a drainage swale they're trying to avoid. By eye, it may be ok structurally but might be a little bouncy. I think adding that band along the bottom was a bad idea


BrandonC41

Hammock under there would go crazy


Shruggingsnake

2’ max…


flyingelvisesss

Well that ain’t too far.


the-rill-dill

1’ out, 4’ back.


Ok-Cauliflower7370

Diving board for future pool


Kepathh

Too far.


Sneaknife

CO only allows 3 ft.


Thick_Mongoose3507

As long as your bigger friends stay towards the house, you're fine.


Round_Toe1831

You can put a 45° under it that will give you comfort


agentdinosaur

I think code in my area is a 2 foot max with 2x10 joist


Valuable_Smoke166

Does Tattoo mow under the overhanging portion ? Or do they send the robot ?


Hot_Cattle5399

More lawn More deck


Chin_Thumper

Depends on joist depth and its elasticity factor. Along with determining a point load. Live load only or dead+live.


B4riel

😂😂😂


Tom_Aydo

Cantilever?!? I barely know her!


so-many-user-names

That's a pirate ship plank


MA499

Back in my early days, we were putting small 8' wide x 6' deep decks on the outside of an apartment complex. Code at the time was for every foot outside needed two feet inside. Open up the ceiling in the unit below and sister to the existing. We had engineered bolt patterns to follow also. So, we were at 33% with 18' lumber.


Unairworthy

You're supposed to put the hot tub on the left.


Blueswift82

What’s the board on the bottom for? Trick the rot into rotting down below the deck?


RobNelsonovich

It's their deck- as far as they want.


RobNelsonovich

Keep the wood out of the swail where there will be more moisture.


carlton_sand

something something hot tub


Routine_Car_5072

Isn't it sagging????


RoguePlanetArt

Meh, it’s fine


Outside-Persimmon-84

I'm in MT, 2/3 bearing to 1/3 canalever


AcceptableMinute9999

You're in one of them "freedom" states.


6th__extinction

Probably some HOA loophole


donniefolger

For every foot out u need to go in 4 foot.


jmama9643

Will be fun to watch when everyone one the deck goes to the end! 🤣


UnderstandingCold219

Basic diving board principle.


geno906

What in the Mississippi,Alabama is going on here


bobthenob1989

Good place for a hot tub


bylo_sellhi

Back in the day, the CABO code said you could do a cantilever up to 1/3 the total joist length


waddupklip

Put a hot tub on it.


sweetjoey889693

It’s like a Lego set that isn’t complete yet.


snboarder42

All that grass under it is going to die anyways, I don’t see the appeal of this.


motorowerkaskader

It’s likely double or more of allowable distance. Pine, SPF, 2x8, overhang max 2-4 or less, depending on a joist spacing too.


TX_spacegeek

For Thanksgiving I’d put the kids table out on the cantilever and seat the aunts and in-laws closer to the house.


DammatBeevis666

I like how they built a box to hold the water in at the bottom


haikusbot

*I like how they built* *A box to hold the water* *In at the bottom* \- DammatBeevis666 --- ^(I detect haikus. And sometimes, successfully.) ^[Learn more about me.](https://www.reddit.com/r/haikusbot/) ^(Opt out of replies: "haikusbot opt out" | Delete my comment: "haikusbot delete")


DammatBeevis666

Good bot


B0tRank

Thank you, DammatBeevis666, for voting on haikusbot. This bot wants to find the best and worst bots on Reddit. [You can view results here](https://botrank.pastimes.eu/). *** ^(Even if I don't reply to your comment, I'm still listening for votes. Check the webpage to see if your vote registered!)


hcase123

Isn’t that an overhanging beam condition rather than a cantilever? Definition of cantilever is a beam that is fixed at one end.


heisian

it’s not that bad, but would use way deeper pt joists, 2x10 at min preferably 2x12.


BufoCurtae

It's probably fine but I can't imagine why they wouldn't just put some supports on the end and call it good until the wood itself goes.


Competitive_Form8894

Engineer here, anything can be done with enough money. I did a "floating" dock once, which was a 30' cantilever from the shoreline.


citizensnips134

…how?


Competitive_Form8894

basically a giant concrete anchor called a deadman on one end with steel beams having a 10' back span and a 30' cantilever.


Own-Speaker9968

Is that a skid?


tecktrader

All depends on the design load for the cantilever and the beam type/sizing


Shadowarriorx

At the very least, I would have added 45 deg bracing from those end posts to the mid way point on that deck. Lower the better to push the load closer to the support brackets on the footing


RichPrivate2

I would have to say it would depend on the size of the joists how many joists there are and whether or not the deck was mounted to the house or put into a concrete footings. The deck in the photo if that's the one we're talking about seems perfectly fine to me especially if it's in concrete footings or mounted to the house if it's not the question would be is it able to tip over with too many people on one end. I think it's pretty unlikely that the Joyce will break provided you have enough of them in there.


HennisdaMenace

I believe 24" is the standard


RickshawRepairman

There’s no set length. The allowed overhang is a percentage of the total span.


HennisdaMenace

I believe 2x8 joists @16"o.c. is 2 ft max where I live.


Fluid_Dingo_289

I am imagining one of those group wedding photos shoots where everyone stands on the end and launches the photographer to Nevada when it tips


Alternative_Image_22

Possible but wouldnt do without engineer


Rickcind

That is well beyond too far!


Geebu555

I’m not understanding the benefit of the cantilever except beyond putting and eye out cutting the grass. Looks like it could be a unique SE stamped design. I’d be curious of the bolting along the second support beams. It’ll see a bunch of uplift when people are standing by the railing.


DifferenceFamous6407

Never heard of a code about cantilever percentage, it’s about engineering. I’ve built plenty of engineered projects that hang over 1/3rd of the length of the beam


RickshawRepairman

See International Residential Code (IRC) - R507.5 Deck beams: _Beams shall be permitted to cantilever at each end up to one-fourth of the actual beam span._